Anyone who has experience with air conditioning systems, I would like your opinion. I am building a new two story house in Havasu. The first floor will be all garage, roughly 2000 sqft. The second story will be all living area, roughly 2200 sqft. I got a few quotes for the A/C/ system. In your experience, is a 5 ton, 14 seer Amana for the living area going to be sufficient? And is Amana a quality unit? And, are two 2 ton, 19 seer Daikin units for the garage going to be sufficient? Are the Daikin units a quality unit? Thanks in advance for your opinions!
 

TPC

Wrenching Dad
Joined
Sep 20, 2007
Messages
30,573
Reaction score
22,883
1 ton Cooling per 400 sq ft.
Vaulted ceilings ya want more in the Southwest.

Amana at one time was the Toyota of appliances.
Dunno if they still make their own or stick their label on someone else’s. Like maybe Lennox.

The current Amana line uses Copeland compressors and inverter technology. Expensive to service in its later years but still good stuff.
Copeland is still a good product.
The new Amanas run quiet.

Daikins nicely made and cheaper to have serviced. They’ve been at it a long time.
 
Last edited:

Riverbound

Banned
Joined
Sep 26, 2007
Messages
26,769
Reaction score
19,255
Anyone who has experience with air conditioning systems, I would like your opinion. I am building a new two story house in Havasu. The first floor will be all garage, roughly 2000 sqft. The second story will be all living area, roughly 2200 sqft. I got a few quotes for the A/C/ system. In your experience, is a 5 ton, 14 seer Amana for the living area going to be sufficient? And is Amana a quality unit? And, are two 2 ton, 19 seer Daikin units for the garage going to be sufficient? Are the Daikin units a quality unit? Thanks in advance for your opinions!

I’m very familiar With both those product lines and you will be VERY happy with them. Only change I would make is to go to the 16 seer minimum for the lifetime unit replacement warranty that Amaa offers. Since it’s a new build, the investment in a 2 stage system in Havasu is worth every penny. So have them bid a 2 stage 16 seer. Should be about $2500 more.
 

Riverbound

Banned
Joined
Sep 26, 2007
Messages
26,769
Reaction score
19,255
1 ton Cooling per sq ft.
Vaulted ceilings ya want more in the Southwest.

Amana at one time was the Toyota of appliances.
Dunno if they still make their own or stick their label on someone else’s. Like maybe Lennox.

The current Amana line uses Copeland compressors and inverter technology. Expensive to service in its later years but still good stuff.
Copeland is still a good product.
The new Amanas run quiet.

Daikins nicely made and cheaper to have serviced. They’ve been at it a long time.

The “Amana” and Goodman AC line is now owned by Daikin and plenty of the technologies have passed through. It’s was a good move and made the products much better.
 

Bobby V

Havasu1986
Joined
Dec 20, 2007
Messages
23,326
Reaction score
12,869
I’m very familiar With both those product lines and you will be VERY happy with them. Only change I would make is to go to the 16 seer minimum for the lifetime unit replacement warranty that Amaa offers. Since it’s a new build, the investment in a 2 stage system in Havasu is worth every penny. So have them bid a 2 stage 16 seer. Should be about $2500 more.
The difference between a 4 ton 14 seer AS / Trane and a 4 ton 16 seer with 2 speed package was $1800 in May. I went in the middle with the 4 ton 15 seer 2 stage over and under package and a Honeywell digital thermostat. My house is about 1700 sq ft.
 

Bigbore500r

Well-Known Member
Joined
Apr 28, 2014
Messages
17,473
Reaction score
35,559
The “Amana” and Goodman AC line is now owned by Daikin and plenty of the technologies have passed through. It’s was a good move and made the products much better.

Thats good to know, I remember Goodman used to be "not so good" 10 years ago. I will say we have 2 at the river and they keep working year after year, although they eat capacitors which i don't think is their fault so much as the Needles power grid
 

Riverbound

Banned
Joined
Sep 26, 2007
Messages
26,769
Reaction score
19,255
Thats good to know, I remember Goodman used to be "not so good" 10 years ago. I will say we have 2 at the river and they keep working year after year, although they eat capacitors which i don't think is their fault so much as the Needles power grid

There is no “junk” equipment. Almost every failure I have ever seen has been due to install issues.
The Goodman stigma was due to them selling to anyone and everyone which led to handymen becoming AC guys and even homeowners doing DIY 🤦‍♂️
 

Bobby V

Havasu1986
Joined
Dec 20, 2007
Messages
23,326
Reaction score
12,869
There is no “junk” equipment. Almost every failure I have ever seen has been due to install issues.
The Goodman stigma was due to them selling to anyone and everyone which led to handymen becoming AC guys and even homeowners doing DIY 🤦‍♂️
My house in Havasu came new with a Goodman. Lasted 7 years. Next was a Trane. Lasted 13 years. Just installed another Trane. I'm sure the semi annual maintenance had helped the last Trane in the Havasu heat. .
 

Inland Air Balance

Certified in something
Joined
May 6, 2008
Messages
949
Reaction score
714
1 ton Cooling per sq ft.
Vaulted ceilings ya want more in the Southwest.

Amana at one time was the Toyota of appliances.
Dunno if they still make their own or stick their label on someone else’s. Like maybe Lennox.

The current Amana line uses Copeland compressors and inverter technology. Expensive to service in its later years but still good stuff.
Copeland is still a good product.
The new Amanas run quiet.

Daikins nicely made and cheaper to have serviced. They’ve been at it a long time.
1 ton per Sq Ft??? Holy shit Batman!!! your gonna need a loan to power that thing! I hope you meant 1 CFM/Sqft.
 

702sandman

Well-Known Member
Joined
Jul 25, 2019
Messages
827
Reaction score
1,894
I typically will use the 400sq ft per ton and here in vegas I would be $2200 per ton on 14 seer trane installed with duct work etc... for the garage I would duct it like a normal system so another 5 ton. 5 ton is pushing it for your living quarters, have you thought about doing a zone system maybe for the bedrooms \ living area.. this would help In my opinion so at night you can turn up the living area a couple degrees and shift more air to the bedroom areas
 

TPC

Wrenching Dad
Joined
Sep 20, 2007
Messages
30,573
Reaction score
22,883
I meant to write 1 Ton per 400 sq ft.
 

TPC

Wrenching Dad
Joined
Sep 20, 2007
Messages
30,573
Reaction score
22,883
1 ton per Sq Ft??? Holy shit Batman!!! your gonna need a loan to power that thing! I hope you meant 1 CFM/Sqft.
You and I have had enough discussions in this forum in threads like these that you know - I know that.
I been at it 44 years.
I edited it for typos and didn’t see I deleted 400 by mistake.
I stand corrected. Bad proof reading.
 
Last edited:

Riverbound

Banned
Joined
Sep 26, 2007
Messages
26,769
Reaction score
19,255
The difference between a 4 ton 14 seer AS / Trane and a 4 ton 16 seer with 2 speed package was $1800 in May. I went in the middle with the 4 ton 15 seer 2 stage over and under package and a Honeywell digital thermostat. My house is about 1700 sq ft.

I quoted union pricing as I thought you were pro union. And paying the increased pricing. 😂👍👍
 

boatpi

Well-Known Member
Joined
Feb 28, 2012
Messages
8,036
Reaction score
11,954
My 18 month old Las Vegas house house about 1
Ton For every 600 square
Feet.
 

Riverbound

Banned
Joined
Sep 26, 2007
Messages
26,769
Reaction score
19,255
Square footage per ton is the worst way to determine system sizing. A heat load must be done and if it’s not you need to hire a competent contractor.
I can do a manual J heat load in about 15 minutes and do one on every house I sell to ensure Proper system sizing.

Using rules of thumbs or averages is a short cut and a large lurchase like this deserves more than a. “guess” from your coNtractor.
 

Wheeler

I'm just here to bitch about others negativity.😁
Joined
Dec 25, 2007
Messages
24,921
Reaction score
39,106
Square footage per ton is the worst way to determine system sizing. A heat load must be done and if it’s not you need to hire a competent contractor.
I can do a manual J heat load in about 15 minutes and do one on every house I sell to ensure Proper system sizing.

Using rules of thumbs or averages is a short cut and a large lurchase like this deserves more than a. “guess” from your coNtractor.

What size increments do ac units come in, ie 1t 2t etc.?

Will a 1 ton 13 seer cool the same space as a 1 ton 19 seer?
 

Riverbound

Banned
Joined
Sep 26, 2007
Messages
26,769
Reaction score
19,255
What size increments do ac units come in, ie 1t 2t etc.?

Will a 1 ton 13 seer cool the same space as a 1 ton 19 seer?

Standard systems in residential come in 1-5 ton range.
Woth .5 ton options 1-3.5

Tonnage is the capacity SEER is the efficiency. Basically think of to age as the horsepower and seer as MPG
 

Wheeler

I'm just here to bitch about others negativity.😁
Joined
Dec 25, 2007
Messages
24,921
Reaction score
39,106
Standard systems in residential come in 1-5 ton range.
Woth .5 ton options 1-3.5


Tonnage is the capacity SEER is the efficiency. Basically think of to age as the horsepower and seer as MPG

Then what I understand it is the benefit of the higher seer # will be cheaper to run?

If tonnage only comes in .5 ton increments and not fractional, how accurate can you be or need to be in sizing a unit ?
 

Riverbound

Banned
Joined
Sep 26, 2007
Messages
26,769
Reaction score
19,255
Then what I understand it is the benefit of the higher seer # will be cheaper to run?

If tonnage only comes in .5 ton increments and not fractional, how accurate can you be or need to be in sizing a unit ?
Correct higher seer will result in a lower per hour cost to run the unit.

it needs to be in the correct range to give proper humidity control as well as prevent short cycling. I factor in around 10-20% buffer whnen I do my
Calcs.
 

LHC Kirby

LifeTime Member
Joined
Jan 12, 2008
Messages
3,431
Reaction score
5,070
INSULATE INSULATE the garage..... I bought the self install stuff for my garage doors in Havasu.... RV 15' and 2 car door 9' . . . . a tad over $500.. WELL WORTH IT..... the idiot builder VERDE HOMES (out of business now) did not insulate any exterior walls.... stupid on my part not to verify when they built it.
 

702sandman

Well-Known Member
Joined
Jul 25, 2019
Messages
827
Reaction score
1,894
If your asking as a general rule of thumb 400 Sq ft per ton will get you close to what you will need, now when we do new construction jobs we hand the plans over to our engineer who does load calcs and man J and S. You will always have the key board warriors that say this or that and they are the best blah blah blah. Go with a company that has good recommendations from people you know and trust and you will be happier in the end. Hope this info helps
 

jailbird141

Well-Known Member
Joined
May 3, 2011
Messages
755
Reaction score
1,416
Thank you for the input everyone. I am going to insist on the higher Seer rating for the living area.
 