Gas Turbine

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
What am I looking at? Wow.
It's a gas turbine engine used as the prime mover for a generator. Next month we tear it down for replacement of the combustion parts. I have plans of posting more at that time.
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
This is the upper half. The first 5 seconds is that of the turbine cover which comes off in several days. We are entering the 28,000 operating hour overhaul or HGP, Hot Gas Path. This consists of removing all parts subjected to the high temperatures. The combustion can cover, fuel nozzles, combustion cans, transition pieces, shrouds, seals and buckets (blades). I will post as things progress.
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Prep in progress. Toll boxes, hooch build, scaffold.
20210310_121421.jpg

20210305_141653.jpg

20210310_090551.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Gas turbine inlet pre & final filter change out. Pre's are 24x24x4 & the finals are 24x24x12". 330 of each. Crew of 9 will have this done tomorrow by 1700. Typically get 15k operating hours between changes.
20210312_104017.jpg
20210312_104212.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
The lift has been pushed to Saturday noon'ish.
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Fuel lines coming off. Night shift is a new crew so not much progress expected. We'll see.
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Correcting insulation and heat trace issues too. This pic shows a burnt heat trace cable. The fix is another layer as the second pic shows. These are the type of failures that can shutdown a power plant. This is not one of those
20210312_090105.jpg

20210312_090125.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
This flange needs attention for the last 2 outages. It leaks steam then stops. It's in the hot position as the pipes grow down. We torque it to 740 ft/lbs in 5 steps. I need to check this guide plate as the pipe now sits in the cold position. If it's getting caught in the I beam I'll have found the issue and correct in November. The cable you see is high temp heat trace.
20210310_092938.jpg
20210310_092923.jpg

Now in the cold position. This isn't the problem.
20210315_124411.jpg
 
Last edited:

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
And we found 3 air leaks. You can't hear this when the plant is running. We'll just replace the hoses and move on.
20210312_114815.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Should have about 42 scaffold structures this time. Our contractor Matt is top notch, he can build anything. Tell him your skeptical and it just fuels him. Typically it's Matt and 1 other starting builds 1 week prior to the outage. I brought him in 3 weeks early this time but ran out of time. Told Matt we need 4 more and it killed him to bring those extras in. Good thing we did, the extras are gone after Sunday and still have 2 large builds to go.
20210305_141553.jpg
20210226_105958.jpg
20210309_153646.jpg
20210309_153639.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Roof came off in 2 picks.
20210313_170620.jpg
 

Attachments

  • 20210313_110822.mp4
    121.5 MB
  • 20210313_123719.mp4
    76.4 MB

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
More hoses removed
 

Attachments

  • 20210313_172247.mp4
    133.9 MB

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Boroscope guy
 

Attachments

  • 20210313_172504.mp4
    29.3 MB

sonicss31

Well-Known Member
Joined
Dec 9, 2018
Messages
2,818
Reaction score
16,155
Instead of filters why not use electrostatic precipitators? Interesting stuff. I just retired from 30years in waste to energy power plant.
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Instead of filters why not use electrostatic precipitators? Interesting stuff. I just retired from 30years in waste to energy power plant.
Good for you on the retirement. I hope to be done in 2 years.
The filters are on the inlet side. I have not heard of precipitators on gas turbines. Aren't those on the stack side? That's about 2.5 years of accumulated dirt. I have seen the conical style go out 8 years but they have more surface area. The DP across the filter is linear until it isn't. I've seen pictures where the filters are so dirty they get sucked into the turbine.
The dirt will plate out on the first 3 to 4 stages of the compressor causing air instability which causes a lose of efficiency and if dirty enough a stall.
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Last night's crew continued pipe removal
 

Attachments

  • 20210314_060838.mp4
    24.4 MB

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
This morning we finished walking down a 120 tag LOTO for work inside the boilers. Up 100ft to the first, back down and up the second, under the boiler for verification of drain valve positions etc. I'm getting too old for this.
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
This beam fell last October from 80 feet up. Put a hurting into the deck. Now time to replace.
20210315_074531.jpg
20210315_075107.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
HP (high pressure 2200psi) SH (superheat) tube bundle
20210314_165800.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
You are looking at the 3rd stage buckets or rotating blades. These grow out when hot and what you see in the second pic is the honey comb seal. These are soft so as the bucket grows it will set its own seal.
20210314_165236_05.jpg
20210314_165536.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Combustion liner, the bottom connects to fwd cap and the top connects to the TP or transition pieces which will be coming next. The slotted end is called the hula hoop seal
20210315_061901.jpg
20210315_061854.jpg
 
Last edited:

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Condenser rupture disc's set to blow out at 5.25 psig. Condenser is under a vacuum to change the steam to liquid. If vacuum gets closer to 0 the stress on the last stage steam turbine blading (L-0) escalates to the point of failure. This is very bad. My last plant suffered this and took 6 months to repair.

20210315_151037.jpg
20210315_150945.jpg
 
Last edited:

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
The yellow is the TPC. Thermal protective coating. This is what has propelled the firing temperature along with the metallurgy of the combustion parts. Back in 1989 the GE Frame 7EA put out 110mw, these 7FA's put out 230mw. The next version put out in excess of 300mw.
20210315_174038.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
The section should be on the ground by 0600 est Tuesday.
20210315_174317.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
It will get rolled over to remove the buckets and nozzles. Bucket specialists will check the moment weights. Each bucket has a serial number that follows the part from birth to death. Typically can be refurbished 3 times which can put a part at 90k operating hours. Moment weights, when inserting a bucket you want the bucket 180 degrees opposite to be extremely close to same weight. These shafts rotate at 3600rpm's. These specialists will open the crates, grab the weight sheet and do their thing. I should be able to get a pic of the sheet.
So the next time your out with an owner of a gas turbine boat ask if the blades are moment weighted.
 
Last edited:

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Fuel nozzles fit into the forward can.
20210315_173746.jpg
20210315_173758.jpg
 

Wolskis

Well-Known Member
Joined
Jan 21, 2008
Messages
802
Reaction score
1,290
Pressure testing the flexible fuel gas hoses. The last thing we need is 500psi gas leaking and going boom. Each hose gets 400psi for 15 minutes twice, with nitrogen in a water bath.
20210315_130801.jpg
20210315_130814.jpg
20210315_130845.jpg
20210315_130841.jpg
 