Never seen one melt like this before.
Never seen one melt like this before. View attachment 636805
It's a 20 amp breaker and number 12 wire, the only thing I can come up with is since the home owner had a rat prob recently, they must have chewed the wires making one of the netrals hot. Ofc it is in a kitchen and it' a sheer wall, with zero access from the other side.
This started out as a bad gfci, when I pulled it that is when I found the double hot going too it. One of the whites in the box is still hot even after disconnecting every thing on that circuit. Getting ready to go in the attic now and trace the wires back.Don't think so on the rat causing a direct short --- a heating, melting like that is usually a high impedance connection that won't trip a breaker, but over time fails --- These are the most dangerous types of failures, often by burning a home. As the connection heats, it creates more resistance, creating in turn more heat. If the failure isn't immediate, the heat damages the conductors and the spring in the connector, resulting in more resistance. Next time it gets worse, so on and so forth ---- it's a cascading effect.
This started out as a bad gfci, when I pulled it that is when I found the double hot going too it. One of the whites in the box is still hot even after disconnecting every thing on that circuit. Getting ready to go in the attic now and trace the wires back.
Yeah has me scratching my head as well. That is why I am really thinking the rats chewed a wire. I can not see them running nuetral thru a curling box some where., luckil the gfci took the a shit otherwise it very easily could have been a fire.Well damn, that is an odd one then. Because the fault that caused the white to become hot, should have tripped the breaker and the damage should have occurred and be evident there, not at the point where the wire nut melted.
Wire nut like that makes me think loose neutral.
The 240 part is odd... some where you have another phase on that neutral.
Sent from my iPhone using Tapatalk
Not a professional a this but if the neutral in the breaker box became disconnected (required to stay hot....) then you are back feeding from anything else on that circuit and using this as your ground?
An Overloaded circuit with loose neutral connection under wire nut can cause meltdown too. Twisting conductor connections together (aka "Cold Soldering") with Kleins before applying wire nuts will help avoid a lot of problems. FYI I remember my apprenticeship instructor saying All UL listed Romex wiring manufactured since 70's has Rat/Mice deterrent built into insulation to prevent gnawing.
Since Grad's just blew this thread sideways to satisfy his need to poke the bear,
Yes, I'm aware of Yellowboat's tales of woe and disappearing Lexuit, but I took this one as sharing a customer's forensically interesting electrical failure. He didn't cause or create the problem, simply trying to diagnose it.I dont think so. Yellowboat has either the worst luck of anyone on eart or a big drama queen. Its always the sky is falling
This ^^^^ with (2) circuits or "A" phase using the same neutral double the load on the neutral=Heat and loose wn will do the same as mentioned.Wire nut like that makes me think loose neutral.
The 240 part is odd... some where you have another phase on that neutral.
Sent from my iPhone using Tapatalk
Since Grad's just blew this thread sideways to satisfy his need to poke the bear, I'll also digress.
This one's right up your "High Voltage" alley.
Years ago I was running a job at a large naval installation, we were replacing all the 15KV UG and primary/secondary substations on the base. Due to it's proximity on the bay and high water table, the manholes were always filled and splices had to be really tight as they had to survive submerged.
Navy contract required a CQC quality inspector on site daily to monitor field work and log everything. Ours was a budding attorney, couldn't screw a nut and bolt together, but with instructions in hand, he'd sure try to tell you how and be ready to torque test as you went. In other words, more often than not, my crews wanted to encase him in concrete for eternity.
We'd just started the splicing and as I approached the manhole I notice my trusty CQC inspector perched by the opening and now I'm seeing rolls of tape and other splicing materials flying up out of the hole --- WTF ? Specs required taped splices and the CQC inspector demanded to watch and follow along with the instructions, at least for the first couple of splices.
So splicer is cussing up a storm, throwing anything he can grab at the inspector, CQC is backing away from the hole to avoid getting hit. Finally get this splicer, who'd been wrapping tape back when I was in grade school, to calm down and tell me what the problem was.
The problem it seems was, the splicer was left handed, the 3M splice instructions were for a righty, so the big fight was over the CQC, sitting there instructions in hand, telling the splicer he was wrapping the tape backwards![]()
The ole guy who could have done these in his sleep, with his eyes covered, was done. By then it didn't matter that I'd convinced the moron inspector the direction of the wrap didn't matter, my best splicer walked off the job.
![]()
That's Hilarious Taboma! I can totally see an inspector saying something stupid like that. He'd make that mistake once. I would've informed him that "Left to right or right to left" doesn't matter, an experienced tape splicer will always push the roll away over the top in order to stretch the tape and avoid "the void" that's important. He can caliper it afterwards and if the taper isn't correct, I'll tear it off and redo it on my dime.
Making me think as you mentioned that's a shared neutral on a 3-wire home run.
I would swap out the breaker. It should have tripped.
Never, only if those neutrals are paired with their specific branch circuit(s). Connecting all neutrals, including ones not associated or paired with the branch hots, creates an extension of the neutral bus, a flagrant violation.Was it not common practice in residential prior to the '99 NEC to tie all neutrals together at any and all boxes ?